    This is some info I have found out on this American Power Conversion UPS. (Uninterruptable Power Supply) I is much same as the "APC Smart 900" but
    does more power as well as a step up or down mains conditioning feature & is fan cooled.

    SCHEMATIC v v v
    ┌────┐┌─────┐┌──────┐ ┌──┴──┐┌───┴────┐_┌───────────┐ ┌───┴───┐ ┌───┐ In>┤12A ├┤Spike├┤Mains ├┬┤ON OR├┤NORMAL/ ├─┤ Large ├┬┤ Smpsu ├─┬┤Bat├> IEC│Trip││Clamp││Filter│││ FAIL││UP/ DOWN├─┤Transformer││└───────┘ ││Mon│
    └────┘└─────┘└──────┘│└─────┘└──────┬─┘ └───────────┘│┌────────┐│└───┘
    │┌──────┐ │┌───────┐ └┤SM Sine ├┴<Batteries
    └┤In Mon├> ├┤Out Mon├> │Inverter│
    v └──────┘ │└───────┘ └───────┬┘
    Out ┌───┴───┐ ┌──────────┐ ┌─────┐ │ ┌─────────────┐ ^
    4x<──┤LOAD ON├─┤Filter Cap├─┤I Mon├────┘ >┤uProc Control├>
    IEC └───────┘ └──────────┘ └─────┘ └─────────────┘

    The control sorts out what is the required state for the 3 relays (CAPITALS) from the various monitoring function inputs. It also predicts battery life.

    It is a switched UPS system, which means there is a very short break (10ms?) in the output when the supply goes out of limits (fails) & the inverter cuts in.

    INVERTER
    The 24V volt inverter uses a powerful bridged Class D 16 FET amp at many kHz.

    │║▓█▓║│ Phase 1 +24V HF pulses
    │║▓█▓║│ fed via the 2
    ~~~~~~~~~~~~~~~~~~~ FET outputs to
    │║▓█▓║│ each side of
    │║▓█▓║│ Phase 2 the transformer.
    ~~~~~~~~~~~~~~~~~~~
    .-.
    / \ These pulses do not get through
    | | the Transfromer with mains capacitor
    | | | so the resultant filtered output is
    | | a rounded mean of those needle
    \ / pulses to make a 50Hz sine wave.
    '-'
    There are several feedback loops that control the output.
    1) The 50Hz is locked in phase to the incoming supply when it is present so
    there is less of a voltage jump on changeover.
    2) Output Voltage feedback ensures regulated voltage.
    3) Over current alarms & then kills the inverter, protecting it from damage.

    BATTERIES
    These are 2x 17AH Batteries, accessed from the pull of front pannel. As with most UPSs of this sort they are literally CAINED to get the performance! So don't expect them to last long. On full load discharge in something like 4 min the batteries are spent, & possibly dammaged! On light loads 1 hr is possable. This UPS has an earthed battery system, there is no connection to the mains as same are. So it is safe to add external large fused batteries. eg. 2 120 lorry batts fused @ 60A beeteen their 12V Link.
    There is DC Safety link on the rear panel to disconnect the inverter.

    FRONT PANEL
    ┌─────────────────────────────────────────────────┐
    │ [] []reduce .·. [] │
    │ [] ( 1 ) [] │
    │ [] [] normal test [] │
    │ [] [] │
    │ [] [] [] .1. [] [] │
    │ [] boost On ( 0 ) Smart Replace [] │
    │ Load Battery '·' Boost Battery Battery│
    └─────────────────────────────────────────────────┘
    The green mains ON LINE LED will be flashing in test node (if
    there is mains present), & the yellow ON BATTERY LED will be on.
    After the 10 second test it will switch back to the mains if it
    is OK, & the green mains ON LINE LED stays on & out goes the
    yellow ON BATTERY LED.

    If mains is just goes a bit to low the yellow SMART BOOST LED
    lights after a second of inverter fill in power.

    If the battery will not accept a charge the red REPLACE BATTERY
    LED is lit up.

    Bargraphs: The battery status bargraph indicates the battery voltage & is a
    good indication of the condition.

    The mains load bargraph lights up as the output loading is
    increased to the maximum 1500W load. (200W/0.8A per LED)

    Alarms: The beeper sounds 4 beeps every 30 seconds after mains fails
    (1/30 seconds initial delay option SW3).

    And when the battery is too low (2min/5min warning) rapid pulse.

    And if the load is excessive.

    Mains Fail: As options set near instant changeover to synchronised inverter on
    failure, e.g. under/over volts, under/over frequency.

    Mains Reset: After 5 seconds of good mains, near instant change back to mains.

    Power off: Just throw the rear ENABLE switch to off. This disconnects the
    output & stops all battery drain.
    Pressing the (0) button only works with no mains, otherwise you
    get a briefly interrupts the output only (dirty changeover).

    Charging: If just charging is needed then leave the rear ENABLE switch on
    without pressing (1) test button.

    As with most things with uProc control that can go wrong & a full power off with battery disconnection may be needed in the worst case. (e.g. before you buy a new set of batteries!) Then do a fresh power up on recharged batteries with a 30% mains load to recalibrate the uProc's battery predictions during the self test.

    See my buls on "APC Smart 900","META HF Melenium 810 UPS", "Lead Acid Batteries", "Constant Voltage Transforemers" & "Mains Power Protector".


    Why don't U send an interesting bul?

    73 De John, G8MNY @ GB7CIP